Question about THD

5.1K views 37 replies 11 participants last post by  OrlyP  
#1 · (Edited)
Hi,

I'm l looking to buy a Firman generator. 2 model is interesting me.

T08072 TRI FUEL 10000/8000W PORTABLE GENERATOR
P08008 GAS PORTABLE GENERATOR 10000W

Both are 10000w/8000w, motor is 439cc on both, looking the same except for the LPN input. This is looking fine.

But one thing is bothering me, T08072 is 11%-14% THD and the P08008 is 25%.
Is it an error in the description or the T08072 really is better ?

Thank you for any advice
Yannick
 
Discussion starter · #6 ·
Problem is I'll buy it for my house, including electronic device such as computers. In fact I already bought the p08008 but the box is still not open. I'm thinking of return it to take the 11-14% thd instead. Those computers are all connected throw a UPS but I dont know how those UPS will react with 25% THD
 
Discussion starter · #15 ·
Ok more clear now. Wrong voltage and frequency is what ups doesn't like. THD is less important that I thought.

To adjust the frequency---> motor speed. Something like that:

And for voltage---->something like that:

In addition, for the THD, all pc's are switching power supply. Meaning they are first filtered and rectified to DC and raise to about 400v dc, and switching it in a transformer as square wave (already noisy). And re-lower down at acceptable voltage with higher current, again, filtered. Knowing this. I agree that THD isn't the worst problem for electronic.

So, turn off the main breaker, start the generator, be sure voltage and frequency is on spec. When all is looking good, turn on the generator breaker.
Thank you for your advice et your time very appreciated.

Yannick