My wife and I live in north central NC (slightly west) in the Piedmont Triad area close to the Virginia state line. We live in a rural area, but only 10 minutes from a Walmart, so it's not too rural, but enough to be out of the big cities and enjoy the countryside. I recently purchased this generator for portable standby service for the house. I have a propane range, hot water heater and heat pump w/ gas furnace assist so this helps ease the power requirements.
I installed a Reliance PB50 power inlet box outside and that is running to a Generac 60 amp manual transfer switch (#6333) in the basement. I swapped out on of the 60 amp transfer switch breakers for a 100 amp (Note: the 60 amp and 100 amp Generac transfer switches are identical except for the breakers they install in them). The transfer switch is then connected to a 100 amp sub-panel that I installed. The reason I swapped out a 60 amp breaker for a 100 amp breaker is so that I could run all the circuits in the sub-panel while connected to the utility side of the transfer switch.
Wired into the 100 amp sub-panel are the following circuits pulled from my main panel(s):
With all of the above circuits switched in (and only one HVAC unit switched in, as indicated) the voltage on each leg from the generator at the 100 amp sub-panel was 118 and 117 per leg. With all the circuits connected and the HVAC switched in last, the generator rpm dipped slightly momentarily and then stabilized. I ran this test for about 30 minutes and there were no issues.
I also unbonded the neutral (white) from inside the generator case to ground (green/yellow).
I installed a Reliance PB50 power inlet box outside and that is running to a Generac 60 amp manual transfer switch (#6333) in the basement. I swapped out on of the 60 amp transfer switch breakers for a 100 amp (Note: the 60 amp and 100 amp Generac transfer switches are identical except for the breakers they install in them). The transfer switch is then connected to a 100 amp sub-panel that I installed. The reason I swapped out a 60 amp breaker for a 100 amp breaker is so that I could run all the circuits in the sub-panel while connected to the utility side of the transfer switch.
Wired into the 100 amp sub-panel are the following circuits pulled from my main panel(s):
- 2.0 ton heat pump (upstairs) & air handler, only one of the heat pumps & air handler will be switched in at any given time.
- 2.0 ton heat pump (main floor & basement) & air handler
- Kitchen fridge, microwave, light/ceiling fan
- Living room lights, receptacles
- Home office w/ various office equipment (needs to be on generator to run our business)
- 2 storage freezers
- Main bedroom lights, receptacles
- Main bathroom lights, receptacles
- stairwell lights
- Front & back porch lights
- Outdoor 50 amp RV temporary power pedestal (only switched in if both HVAC's are not connected)
- Various other small current draw circuits for other areas of the house
With all of the above circuits switched in (and only one HVAC unit switched in, as indicated) the voltage on each leg from the generator at the 100 amp sub-panel was 118 and 117 per leg. With all the circuits connected and the HVAC switched in last, the generator rpm dipped slightly momentarily and then stabilized. I ran this test for about 30 minutes and there were no issues.
I also unbonded the neutral (white) from inside the generator case to ground (green/yellow).