I have a DuroMax XP12000E generator (12,000 W starting, 9,500 W running). In the manual’s specification section, DuroMax says:
With DuroMax claiming a floating neutral, with nothing connected to the generator, I measure zero ohms from neutral to the ground pin, indicating the neutral is bonded to the green safety ground, but infinity ohms from the neutral to the generator support frame.
Is DuroMax lying about having a floating neutral? More importantly, do I have a safety problem here if I connect that generator to the house in case of a major power outage?
With DuroMax claiming a floating neutral, with nothing connected to the generator, I measure zero ohms from neutral to the ground pin, indicating the neutral is bonded to the green safety ground, but infinity ohms from the neutral to the generator support frame.
Is DuroMax lying about having a floating neutral? More importantly, do I have a safety problem here if I connect that generator to the house in case of a major power outage?