Failed Generac 7kW 0058370 and Researching Solution

13K views 73 replies 11 participants last post by  kingbellaus  
#1 ·
Hi, folks.

I'm new to the forum, and while I'm fairly hands-on with mechanical equipment, I'm not an expert on generators. So. I would appreciate some help in making the next move in ensuring reliable standby power for my home. Please accept my apologies for the long post!

Here is some background:

The house was built (for the previous owner) in late 2014, and was equipped with a Generac Model 0058370 unit with ATS. Not sure what model the transfer switch is, but I have included some pictures to help identify generator and ATS:

Image


Image


We've owned the home for about 4.5 years, and generally experience probably about 5 power outages per year, most of which are 4 hours or less. I have maintained the unit with synthetic oil, new filter, new plug, new air filter, etc., annually, and it has been fairly trouble-free. The only ongoing issue we have experienced is slow starting. The unit will always start, but it takes a lot of cranking before it will fire, usually right at the end of the first cranking cycle. This likely contributed to an early failure of the starter, which I replaced last year. The generator is on propane, and we are currently operating with 100lb cylinders, which last quite a long time. As far as requirements, we do really need an automated solution as our house we have a couple of sump pumps that are important at certain times of year.

Fast forward to two days ago. In our area, we have experienced heavier-than-normal snowfall, and with overhead lines in a heavily-forested area (Vancouver Island, BC), we have seen more frequent (and longer) outages than normal. This includes 14 hours over two outages on Christmas Eve. On Sunday morning, we had a very short outage, the generator started, and then horrible noises quickly ensued. Before I could get anywhere near the machine, it had obviously suffered catastrophic engine failure, which was confirmed when I looked inside the enclosure.

Image


Ouch.

Not sure of the cause, as I did check the oil regularly, but I understand from internet research that this sort of failure is not uncommon for these units. The local Generac dealer confirmed this, and says that engines (and many regular parts) are no longer available for this model. He also confirmed that comparable replacement units are taking about 45 weeks to arrive due to global supply chain issues. C'est la vie.

So, for short-term coverage, I picked up a Firman 10000/8000 dual fuel unit (it was available down the street), and have it running, with extension cords handy, to get me through until I have a better, solution. For the slightly-longer term, I was thinking of simply connecting the Firman unit with a 230V twist-lock connector in place of the hard-wired connector that went to the Generac unit. However, this brings me to the first question:

If I understand correctly, in the even of loss of line power, the transfer switch commands the generator to start, and when it sees AC power from the generator, it transfers the load to the generator. Is this accurate? I have found manuals online that I think are the correct ones for this setup, but I just want to be sure.

If my understanding is correct, I would assume that if I connect the Firman unit to the cable that was going to the Generac, when the power goes out, I should be able to go manually start the Firman, and when the transfer switch sees it come up, then it will automagically switch over to generator power? Is this accurate, or am I missing something? Is there any logic exchanged between the generator or the ATS. or do they have to be a matched set, for some reason?

Unfortunately, the Firman unit doesn't have a remote start option, so I won't be able to (easily) make that work, but at least this lets me get going without having to worry about all the extension cords, for now.

I have some ideas about where to go from here, but this post is already too long, so I will end it here for now, and will add some additional thoughts and questions a bit later.

Thanks in advance for your patience with my noob questions.

Cheers,
Shaun
 
#58 ·
Hi, folks.

Well, a lot of time has passed, and I haven't had much time to work on the project, but I have finally accomplished phase 1 (generator in enclosure with manual start/transfer). Here are a few pictures:

Image

Image

Image

Image


I just realized that I didn't grab a pic of the fan and louvers from the inside. Will do that.

I think it looks pretty reasonable, and it looked even better once the silicone had dried to clear. There's definitely no hiding what's inside, but that's not unexpected. :) I also notice that the lid of the enclosure looks a bit distorted in these pics, and it is, but that is because it was propped up on one side during all the installation work. It very quickly returns to its normal shape once it is allowed to lay flat for a few minutes.

Overall, I'm happy with how it turned out, and operating noise is quite well-contained. Interior temps seem to be very reasonable so far, but I'll definitely do some additional testing to be sure. The fan/louvers seem to be working well, and the exhaust heat is minimal. The exhaust inside the shed is built in layers with a flexible steel extension running to the outside of the shed, surrounded with a layer of ceramic fiber insulation, and then the metal dryer vent outlet around that. I still have some more testing to do, but after running for about 30 minutes, the exhaust was warm (of course), but I could still leave my hand on it for a second without issue. This was on a 33C/91F day, and it seems very reasonable to me.

Next step will be to get going on the inverter/charger unit so the generator can be relegated to backup charging duties. The batteries took about 3 months to arrive, but I now have pretty much all that I need to progress, and I want to have phase 2 in service before winter.

Sincere thanks to all who have provided input so far!

Cheers,
Shaun
 
#59 ·
From the perspective of monitoring temps inside the enclosure, I'd appreciate any input on options for suitable thermometers. Ideally, I'd love to have something in there permanently that would monitor temperature and report alerts (via WiFi) when things exceed established thresholds. Any suggestions?

Cheers,
Shaun
 
#60 ·
Plenty of options online: Amazon.com : remote temperature monitor with alarm

In my case, I use a combination of products because I already have other IoTs and smart devices at home.

I use these Zigbee sensors and put them in every room in the house. You could put one inside your generator enclosure:

Then you'll need one of these hubs to which the sensors connect to (via Zigbee) and connects them to the internet (via WiFi or wired ethernet).

or


Finally, you'll need the app for the above hub of your choice (whether it's Tuya/Smart Life or eWelink/SonOff) on your phone to set them all up, which also lets you integrate it with voice assistants such as Alexa or Google Home. It enables you to ask "Alexa, what is the temperature (or humidity) in the bedroom?", etc. If you don't need that, the app lets you set it up in such a way that it can notify you when a certain temperature or humidity threshold is reached. If you have smart devices, in addition to sending you a notification, it can also do things like or turn a light on, like a colored smart bulb (ie. light it up RED as a visual warning for anyone in the house) or turn on a 2nd exhaust fan in the enclosure, etc. Compared to using a basic remote thermometer/hygrometer, these smart devices are much more flexible.... if you're that guy. ;)
 
#62 · (Edited)
Hello everyone I just bought a home.I have never had a standby generator. this is my first one, and I know I have to do the annual maintenance,, coming up I think I'm going to do it next week¡ I have no idea when it was last maintained¡ we did have a power outage today The machine did not start on its own... We had one other power outage since we've been here,,, and we've only been here two months¡¡… It started on its own worked the first time… this time I came home all power was out …so I went out and I checked …¡I put it into manual It started up and then I quickly decided to shut it off,, and figure out why it didn't start on its own… I pulled the fuse on the board it was fine,,, I put it back in ,,check the oil it was low…¡ I filled it up put it back on auto and it started up and worked fine¡¡… My question is with the panel the top light is solid green stating systems go,,,, but all the buttons below it are flashing red¡¿¡¿ It was not doing this until I pulled the fuse did I do something wrong? ¿¡¿Also does anybody have a part number or website in which to get a kit for maintenance oil change air filter etc?? Thank you so much for any and all help in advance¡¡¡¡
 
#67 ·
I have no idea when it was last maintained
My question is with the panel the top light is solid green stating systems go,,,, but all the buttons below it are flashing red
Since you don't know the maintenance history of the unit, I would recommend having the battery load tested. The Corepower units don't have a smart charger and the batteries tend to not last more than 3-4 years.

Regarding the flashing lights, the gen may not have the exercise time set. See this.

If you don't have the manuals, the owner manual is here, and the diagnostic manual is here.

I think the correct maintenance kit is this.
 
#68 ·
Thank you so much! I really appreciate your help! I have spent quite a bit of time on Google trying to find the information there, but I guess the unit is to old. Some of it matched up, but did not want to trust partial information. I made both posts at the same time. I am part of a few forums. But a lot of forms I've tried joining ,didn't have very many people answering questions after theirs were answered. But thank you for your help and time! I really do appreciate you!
 
#70 ·
buy a "unit" to make it "smart" is this possible with this unit?
I don't see any reason that you should not be able to do that since the battery trickle charger is independent of the control board.

Image

I would recommend a smart charger like this one, this one, or similar. I would use a smart charger that has at least 3A capability since it has to supply the gen with 12VDC when it is running or not. Smart chargers can safely be left on the battery 24/7 without the potential damage that trickle chargers cause.

You could do an easy install by cutting off the leads on the existing charger and the smart charger, and then splicing it in with soldered joints and heat shrink. A more complicated way would be to install a 120V receptacle inside the gen that is fed by the 120V wiring of the existing charger.

Be sure to disconnect power to the gen before working on it. Pulling the fuses in the transfer switch should do that, and then double-check with a meter that the gen does not have power.
 
#71 ·
I don't know how you do the "this" with the link attached to it! but it honestly the coolest thing to me! Lol I am probably going to just spice the charger for now. I have a friend who is a electrician that is going to help me run outlets inside the house, I may see if we can add that to the list! I know this unit is old but we just bought the house. I've been looking at newer units. I know this one may not have long to go. I'm really hoping it does, odviously lol... But I doubt it. Especially after seeing it so low on oil the other day.... But I really appreciate your help! I did download and print off the manuals. Thank you for that again! I also got the weekly "auto run" set now! Thank you so much for all your help!
 
#74 ·
When I ordered that kit, I was trying to like "cross reference" the parts. Every where else the filter was like 30-40$ and pretty much the same with the oil filter! The set came and it's all genuine gerac parts! I was not expecting that! Thank you again for you help!! I printed off the manual and troubleshooting manual, went threw and highlighted and made notes. Got to find my gap tool now lol