I imagine the power wiring from your generator to the transfer switch is sized to the 7kw generator, so that's something.

I'd think you'd want to make sure the current generator is totally out of the mix, so I think I'd disconnect all electrical connections from the transfer switch, in preparation to operate it manually.

Where's the Firman sit when it's in operation, and where's the transfer switch, inside or outside?

I mean, you could drill a hole in the existing gen's enclosure and mount the inlet box, if you could conveniently wheel the portable in the vicinity.

I'm fuzzy on all this stuff, but the transfer switch has a 50 amp breaker, but the nameplate say 29.2a at 240v. So, I wonder if you might be okay with a 30amp 240v. twist lock inlet. The Firman's 30 amp plug would have a breaker on it too, right? Things would be cheaper.