i believe i have an older generac 7500 gas generator, with a few 110 plugs, a round 3 prong 110 plug and a round 4 prong 220 30 amps plug, i have a Miller stick welder that can draw up to 50 amps, my question is, can I some how get the generator to put out 50 amps or even 40 amps out of the 220 so i can use it to run my welder?

i have used it to run my welder with alot of circuit breaker popping, and the idle control does not work, which i know makes no difference (better for me because of less lag when i strike up an arch)
if this is possible i can get all the info you want off the generator but if not just let me know and i wont bother,
Thanks Yall
 

·
Registered
Joined
·
69 Posts
You can't. It's that simple. 50A x 220v equals 11,000 watts. Add 1/3 for overload protection you need a 15k generator to run that welder.
 

·
Registered
Joined
·
2 Posts
Discussion Starter #3
so i could only get mabe 35 amps out of it max?

i also have another identical 7500 generac and 2 smaller hondas with only 110 plugs
my welder can also run 460, can i get 220 or 460 50 amps by wiring both generators to a box?
thanks again
 

·
Registered
Joined
·
400 Posts
so i could only get mabe 35 amps out of it max?

i also have another identical 7500 generac and 2 smaller hondas with only 110 plugs
my welder can also run 460, can i get 220 or 460 50 amps by wiring both generators to a box?
thanks again
No, you can't do this.

When using AC it isn't like putting batteries in series. The frequency has to be exactly right and synchronized on all the sources.
 