Discussion Starter · #1 ·
Hi,
Looking for some guidance please, want to get a generator to power a 5 ton AC unit and a few items like fridge, internet, some lights.

I want to add a Transfer Switch, however, the 5 ton AC's breaker is in the main panel next to the meter, which is on the outside of the house and the other circuits are in a sub panel in my garage.

Is it even possible to run the AC and the circuits to the xfer switch?

Thanks...
 

·
Registered
Joined
·
375 Posts
Hi,
Looking for some guidance please, want to get a generator to power a 5 ton AC unit and a few items like fridge, internet, some lights.

I want to add a Transfer Switch, however, the 5 ton AC's breaker is in the main panel next to the meter, which is on the outside of the house and the other circuits are in a sub panel in my garage.

Is it even possible to run the AC and the circuits to the xfer switch?

Thanks...
Look at an interlock kit for your main panel. Usually the generator breaker goes in the top slot, so you may need to move some circuits further down the panel. You'll also need a soft start kit for an AC that large. Check out the MicroAir EasyStart 368. I have a 4-ton AC and my Honda EU7000is won't run it. You're going to need a large generator...probably in the 10-15kw range.
 

·
Registered
Joined
·
76 Posts
What's your budget? You can make almost anything work with deep pockets. Generator by the utility entrance along with the transfer switch. Run the entire house on a generator.
 

·
Registered
Joined
·
455 Posts
I think you will have to install a sub panel and put the breakers in it for the devices you want to power.
The process is easy, but requires a licensed electrician to do the work.
 

·
Registered
Joined
·
418 Posts
I want to add a Transfer Switch, however, the 5 ton AC's breaker is in the main panel next to the meter, which is on the outside of the house and the other circuits are in a sub panel in my garage.
If I am reading what you typed correctly - there are only 2 loads on your "main panel" (IE - "service entrance" panel). 1 - your AC, 2 - the feed to your interior "sub panel".

Adding a transfer switch to this set up wouldn't be at all any different than a single panel - if you are doing a whole panel transfer switch**. Once you get the source (utility or generator) to the main panel everything down stream is the same circuitry as you have now.

**There are transfer panels you can get that will isolate your key circuits and only transfer these circuits, as opposed to the whole panel. This is a totally different set up and I am assuming this is not what you are after - you are after a whole panel transfer switch.
 

·
Registered
Joined
·
3 Posts
Discussion Starter · #6 ·
Thanks for the input everyone, much appreciated. I should have clarified, the main panel not only feeds the sub panel, but the 2 ac units, pool, exterior gfci circuit and also another 60A panel that I mainly use for Christmas lights 🤣
@Browse Deweb, thanks for the info on the Easy Start, definitely something I should do regardless.

Im here in Texas and with the ice storm and most likely rolling blackouts coming, wanted to get a generator to power the 5 ton AC unit and just a few critical circuit.

My plan was to put the transfer switch next to the sub in the garage, add the few critical circuits (fridge, some lights) and them somehow figure out how to add the 5 ton AC unit to it. Would I have to run a line from the AC breaker on the exterior panel to the transfer switch? Definitely not trying to power the whole house.

Thanks again, appreciate all of the input!!!
 

·
Registered
Joined
·
3 Posts
Discussion Starter · #7 ·
Look at an interlock kit for your main panel. Usually the generator breaker goes in the top slot, so you may need to move some circuits further down the panel. You'll also need a soft start kit for an AC that large. Check out the MicroAir EasyStart 368. I have a 4-ton AC and my Honda EU7000is won't run it. You're going to need a large generator...probably in the 10-15kw range.
That's strange, a 4 ton even with 10 SEER should be 4kw and maybe up to 6500 on start up, shouldn't that Honda handle it? I could be missing something on the calculations.
 

·
Registered
Joined
·
375 Posts
That's strange, a 4 ton even with 10 SEER should be 4kw and maybe up to 6500 on start up, shouldn't that Honda handle it? I could be missing something on the calculations.
It pulls 129 amps on startup (LRA) and runs at about 22 amps @ 240V. The Honda is running on natural gas, so it can only provide about 5kw continuously. Even if I had a soft starter on it, I wouldn't have any power available for other things. I don't want to run the Honda that hard during an outage.
 

·
Registered
Joined
·
76 Posts
It really doesn't matter how many sub panels you have downstream of your utility entrance as long as you use a transfer switch at the utility entrance. If you don't want a generator capable of powering everything at one time you can manually switch off breakers for non-essentials. That's what I was doing when my EU7000is was the sole emergency power source, the Honda is wired into the house load center and doesn't power my garage and pump house/well.
 

·
Registered
Joined
·
4,833 Posts
Thanks for the input everyone, much appreciated. I should have clarified, the main panel not only feeds the sub panel, but the 2 ac units, pool, exterior gfci circuit and also another 60A panel that I mainly use for Christmas lights 🤣
@Browse Deweb, thanks for the info on the Easy Start, definitely something I should do regardless.

Im here in Texas and with the ice storm and most likely rolling blackouts coming, wanted to get a generator to power the 5 ton AC unit and just a few critical circuit.

My plan was to put the transfer switch next to the sub in the garage, add the few critical circuits (fridge, some lights) and them somehow figure out how to add the 5 ton AC unit to it. Would I have to run a line from the AC breaker on the exterior panel to the transfer switch? Definitely not trying to power the whole house.

Thanks again, appreciate all of the input!!!
look in to portable room ac units for when you are on gen set.
way lower on the power required.
how many square feet is the house?
 

·
Premium Member
Joined
·
1,438 Posts
I’m a big fan of the microaire soft starts. I have one on my 3.5 ton unit. 120LRA. No dimming lights, the the AC turns on, and it’s easier on the motor windings, potentially adding longevity To the compressor. My eu7000 can start the unit easily if I have my eu2000 paralleled with it. (Not recommended)…
 

·
Registered
Joined
·
50 Posts
I’m a big fan of the microaire soft starts. I have one on my 3.5 ton unit. 120LRA. No dimming lights, the the AC turns on, and it’s easier on the motor windings, potentially adding longevity To the compressor. My eu7000 can start the unit easily if I have my eu2000 paralleled with it. (Not recommended)…
Wow, how are you doing that with 240VAC? I thought the EU2000 is only a single phase. Would have thought that you'd have to have a larger inverter generator that had an L1 & L2 phase? Or are you just doing it on one phase...so you can load that side a little higher?
 

·
Registered
Joined
·
375 Posts
Wow, how are you doing that with 240VAC? I thought the EU2000 is only a single phase. Would have thought that you'd have to have a larger inverter generator that had an L1 & L2 phase? Or are you just doing it on one phase...so you can load that side a little higher?
Here's a video of a guy doing this:

The smaller generator reduces the loading on the larger generator by the looks of the displayed output.
 

·
Registered
Joined
·
4,833 Posts
yea the little gen is on the side that has the 120 volt stuff for the hvac fans.

i lock my hvac blowers to on when i am on gen set.
that helps!
 

·
Registered
Joined
·
3 Posts
f
Hi,
Looking for some guidance please, want to get a generator to power a 5 ton AC unit and a few items like fridge, internet, some lights.

I want to add a Transfer Switch, however, the 5 ton AC's breaker is in the main panel next to the meter, which is on the outside of the house and the other circuits are in a sub panel in my garage.

Is it even possible to run the AC and the circuits to the xfer switch?

Thanks...
Instead of confusion you can through review sites.
 

·
Registered
Joined
·
172 Posts
I had decided against the expense of a manual service entrance transfer switch. But Ida made me reconsider. I could be in my current location longer AND I unexpectedly inherited a small amount of money, enough for this. I went ahead and bought an EZ Connect 200amp transfer switch. You have to get the models with the breaker to be "service entrance rated." The model I purchased is the EZC-M200, EZ-Connect with no inlet (200A) and 200A disconnect. I already had an inlet box and didn't think the way they have the plug on the side of the box is rain proof, like box I have. The switch is a large box, almost 2 feet long by about 14.5 inches wide. This is same company that makes Generlink. I purchased the switch from Home Depot but you can purchase it directly from them. Also, after looking at the wiring of my generator, it will be simple to just wire the generator it's 75amp breaker directly to the switch at a later point. Electrician is coming in the morning. Not sure when he will do it. I am guessing, since the red tag on the panel from the power company will have to be cut, that he will have to do some sort of planning and thus not do it tomorrow. This will allow me to ultimately get the full 27000 watts starting and 18000 watts running power out of my generator and power at least one of my central AC units. Audio equipment Font Electronic instrument Machine Electronic device
Wood Rectangle Font Material property Gas
 

·
Premium Member
Joined
·
1,438 Posts
I had decided against the expense of a manual service entrance transfer switch. But Ida made me reconsider. I could be in my current location longer AND I unexpectedly inherited a small amount of money, enough for this. I went ahead and bought an EZ Connect 200amp transfer switch. You have to get the models with the breaker to be "service entrance rated." The model I purchased is the EZC-M200, EZ-Connect with no inlet (200A) and 200A disconnect. I already had an inlet box and didn't think the way they have the plug on the side of the box is rain proof, like box I have. The switch is a large box, almost 2 feet long by about 14.5 inches wide. This is same company that makes Generlink. I purchased the switch from Home Depot but you can purchase it directly from them. Also, after looking at the wiring of my generator, it will be simple to just wire the generator it's 75amp breaker directly to the switch at a later point. Electrician is coming in the morning. Not sure when he will do it. I am guessing, since the red tag on the panel from the power company will have to be cut, that he will have to do some sort of planning and thus not do it tomorrow. This will allow me to ultimately get the full 27000 watts starting and 18000 watts running power out of my generator and power at least one of my central AC units. View attachment 10170 View attachment 10171
Looks good, simple and effective. So your plan is to hard wire a cord/cable from the generators 75amp breaker to the switch without a connector??
 

·
Registered
Joined
·
172 Posts
Looks good, simple and effective. So your plan is to hard wire a cord/cable from the generators 75amp breaker to the switch without a connector??
That was the plan. Electrician just left and shot that idea down. He didn't elaborate but strongly advised against wiring off the 75amp breaker. My house is bit on the larger size with a 4ton and 3.5 ton central air, upright freezer and separate refrigerator, washer and electric dryer, free standing ice maker, 6 wall mounted tv's, 10 ceiling fans, etc. You get the picture. He was cautious that I could easily overload the generator. He has to assume I'm stupid right? You never know what level of knowledge the client has or what their behavior will be. Also suggested I bury the cable and not use the soow cable I have because it would have been easier. I bought an soow cable because I knew I could resale it if anything changed and I expected I might not want to be locked in to 50 amps.

It's likely that I will at least add a 60 amp breaker to the generator and buy a bigger soow cable. There is some redundancy there, a cheap 75 amp Chinese made breaker followed by a cheap 60 amp breaker. At least that way the 75amp breaker is not the sole thing that is preventing the generator from overloading and catching fire. It would be different if I were using a circuit panel mounted 50 or 60 amp breaker to connect the generator. Then I'd still have two breakers preventing an overload. With the service entrance transfer panel, it's just going all into the house and the only breakers preventing the generator from overloading are the ones on it.
 

·
Premium Member
Joined
·
1,438 Posts
I’d rather you don’t hardwire it either. Definitely can’t blame that electrician for airing on the side of caution. Lots of knuckleheads out there.

I know you are eager to implement a setup that capitalizes on more of the generators capacity. But maybe it’s prudent to stick with the 50 amp connection and observe how things work out while planning for a more complete system.
 

·
Registered
Joined
·
5 Posts
I’d rather you don’t hardwire it either. Definitely can’t blame that electrician for airing on the side of caution. Lots of knuckleheads out there.

I know you are eager to implement a setup that capitalizes on more of the generators capacity. But maybe it’s prudent to stick with the 50 amp connection and observe how things work out while planning for a more complete system.
Here's a link. I just got done checking this info to verify is my gen can handle the AC.

 