Discussion Starter · #1 ·
Have a Cat RP800E that the co system is fried. I have emailed Cat trying to find small controller box with 8 pins it does not show it on parts list. They have not yet to get back to me. The Carbon monxide warning system I would like to wire around.
JANXIN
B09SA-002
35659-YA70110
S1906204
2019062600453
This is whats on controler, have not been able to find anything
Whats your thoughts?
 

·
Registered
Joined
·
4,135 Posts
maybe you dropped a zero?
Cat RP8000E should be the model?
try just unplugging the c/o sensor and see if the gen runs.
 

·
Registered
Joined
·
4,135 Posts
click here take a look at this page
that is the factory cat page on this gen series
the owners manual as well as the service manual is on that page.

you can bypass the c/o detection for service shop testing.
and proving that the c/o unit is bad.
but for real world use do not by pass them as they are for customer protection.
 

·
Premium Member
Joined
·
1,099 Posts
I’m pretty sure all these CO sense generators can operate with the box unplugged.
 

·
Registered
Joined
·
4,135 Posts
I’m pretty sure all these CO sense generators can operate with the box unplugged.
most are setup that way...
at least for now.
you can trace down the wires and clip the shut down if the unplug does not work for test.

state fire code might not like disabling a safety feature as well as your insurance company in case of a claim.
 

·
Registered
Joined
·
4,135 Posts
the c/o ckt has one wire that grounds out when c/o is detected
see the links i sent for those manuals, or pm for more info.
 