Any benefit to liquid vs air cooled standby 22KW

I'm in pre-purchase phase on a residential standby unit. I'm at 22KW requirement and see that generac offers both air cooled and liquid cooled units at this capacity.

Of course, liquid cooled is $5K additional. Is there any reliability or run-time benefit to liquid cooled vs air cooled? My target in the southeast is 7 day run time. Both can do that but air cooled is cheaper, better fuel use, quieter. Is there a reason to spend more?
MikeBW is offline  
Sponsored Links
Advertisement
 
post #2 of 15 (permalink) Old 11-11-2019, 07:25 PM
Senior Member
 
tabora's Avatar
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 299
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 50 Post(s)
Quote:
Originally Posted by MikeBW View Post
I'm in pre-purchase phase on a residential standby unit. I'm at 22KW requirement and see that generac offers both air cooled and liquid cooled units at this capacity.

Of course, liquid cooled is $5K additional. Is there any reliability or run-time benefit to liquid cooled vs air cooled? My target in the southeast is 7 day run time. Both can do that but air cooled is cheaper, better fuel use, quieter. Is there a reason to spend more?
I guess the question is where exactly are you located and what temperatures do you anticipate enduring while running for 7 days? Liquid cooling is likely to deal with higher temps better than air cooling does. At 22KW, you're at the very top end of air cooled generators, and the bottom end of liquid cooled.
https://www.americasgenerators.com/b...nerators-.aspx
tabora is online now  
post #3 of 15 (permalink) Old 11-12-2019, 12:30 AM Thread Starter
Junior Member
 
Join Date: Nov 2019
Posts: 3
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 2 Post(s)
Thanks. I understand 22KW is the typical cutoff between air and liquid cooling. I'm in Miami looking for multiday post-storm backup. Since Generac makes a 22KW in air cooled and water cooled unit, I was wondering if the benefits of a water cooled unit are worth the almost two-fold price. I also understand annual maintenance costs will be greater.

I would be willing to pay a premium for robustness and dependability and longer run times. However I cannot find hard facts that water cooled units provide such benefits and was hoping some pros would have some real life observations on this.
MikeBW is offline  
Sponsored Links
Advertisement
 
post #4 of 15 (permalink) Old 11-12-2019, 07:44 AM
KRE
Senior Member
 
Join Date: Nov 2011
Location: NE. Alabama
Posts: 318
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 41 Post(s)
Never base your final generator choice on price, or an ad. Talk to those who have what your looking at, to see if their money was well spent or otherwise. Once you get above 12 KW I would suggest never buying anything above 1800rpm or any gen set with a built in transfer switch. Buy once an cry once, as paying for a quality back up power is way cheaper up front vs the back side. Plus not having it available when it's needed most is sicking, plus can be dangerous depending needs.
HarryN likes this.

Once you know how a device, system, ect operates, finding the root cause in the event chain is easy. Until then, you will always be chasing/repairing the effects. Learning is a life time event, if you want to outsmart, whatever item you want to repair.
KRE is offline  
post #5 of 15 (permalink) Old 11-13-2019, 12:48 AM
Senior Member
 
Join Date: Jun 2015
Posts: 208
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 27 Post(s)
Curious why you need 22KW when most of us get by on a lot less?? Is that a realistic assessment of what you actually need in an outage or a "worst case, belt and suspenders" approach? Certainly a liquid cooled unit is going to be a better quality than a air cooled unit, question is do you need that kind of quality and reliability? "South East" probably means you have to deal with Hurricane related outages, evaluate how often and duration you've experienced into your equation. Balance the preceding questions against your finances.

Good luck,
.
exmar is offline  
post #6 of 15 (permalink) Old 11-13-2019, 07:18 AM
KRE
Senior Member
 
Join Date: Nov 2011
Location: NE. Alabama
Posts: 318
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 41 Post(s)
20-25kw is a normal size for a average home package. Once you add up all that could be on at one time, or if you heat with electric it can add up quick. There are homes in this country that have much larger units installed, depending live style based on needs or wants. The largest I've ever installed an commissioned was a 350KW Onan in a home in Miami Fla. It took all of it to run that home, pool heaters, atrium A/C units, elevators, kitchen, ect. My home unit is a 25KW I built from scratch, an many times while working in the shop it will peak at 23.5KW with the home running, plus a lathe, welder, planer, running at the same time. Many homes are used for work places, as well as entertainment. The last thing you need is for the power to go off an stop a project from being completed on time, or kill a business party. Then add the fact if the power goes off an you are away, you could lose everything in your freezers, or have the basement full of water, or busted plumbing do to freezing upon return. Many people see whole home backup power as a safety net, that does not require baby setting.
captaindomon likes this.

Once you know how a device, system, ect operates, finding the root cause in the event chain is easy. Until then, you will always be chasing/repairing the effects. Learning is a life time event, if you want to outsmart, whatever item you want to repair.
KRE is offline  
post #7 of 15 (permalink) Old 11-13-2019, 08:23 AM
Senior Member
 
Join Date: Jan 2019
Posts: 101
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 28 Post(s)
If you used that amount of power all at once, your bills would cost a fortune.. You might use a fraction of that at once Im guessing

Last edited by speedy2019; 11-13-2019 at 08:25 AM.
speedy2019 is offline  
post #8 of 15 (permalink) Old 11-13-2019, 12:59 PM
KRE
Senior Member
 
Join Date: Nov 2011
Location: NE. Alabama
Posts: 318
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 41 Post(s)
Quote:
Originally Posted by speedy2019 View Post
If you used that amount of power all at once, your bills would cost a fortune.. You might use a fraction of that at once Im guessing
Well lets look at that. Let's just say it's a total electric home in the Midwest. The heat pump is having issues keeping up with the cold so now the emergency heat strips come on. That by it's self could be 7-15KW alone then add the fan at 0.8-1.2 kw running an now we are at 7.8 on the bottom side an 16.2 on the top side. The Freg is now wanting to run as well as the freezer kicks on that adds another 1.8-2.7 depending size an model. So now it's 9.6 to 18.8KW then the Water heater comes on another 3.2 to 4.5 KW here we are now at 12.8 to 23.3 an the TV, radio, or any battery charging has not been added yet. Can one live with a rope start sure, but your going to be w/o many things an/or playing, what do/can I power now? If you do not heat via electric a 15kw genset is the norm for up to 2K sq ft, assuming no large shop tools are involved. Also remember reactive inrush is a hard number the genset has to deal with, if you can fully control when inrush happens yes a smaller set will suffice. This can be done with device preference lock outs, interlocks, or load shedding devices properly installed. Once you get past XXX dollars for backup power it does not cost that much more to do the whole home properly. The draw back is if you have a quality whole house set an the power is out for 3 days plus, you will not believe the number of people who want to be your best friend/s. BTDT Most power Co's (utility's) size the average home at 5-6.5 KW as not everything is not on at once an many homes have no one home 24/7.

Once you know how a device, system, ect operates, finding the root cause in the event chain is easy. Until then, you will always be chasing/repairing the effects. Learning is a life time event, if you want to outsmart, whatever item you want to repair.
KRE is offline  
post #9 of 15 (permalink) Old 11-13-2019, 04:24 PM
Senior Member
 
Join Date: Jun 2015
Posts: 208
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 27 Post(s)
My neighbor has a three bedroom house, electric heat, water heater, dryer, etc. the 13KW has worked just fine for about ten years. He does have a gas range which helps some. I have a similar house with gas heat and got along fine with a 3500W, upgraded to a 5500W. Don't use the electric dryer during outages which usually are a couple of hours up to 1-2 days.

Comes down to how often outages occur, willingness to deal with small inconveniences and how much you want to spend.
exmar is offline  
post #10 of 15 (permalink) Old 11-14-2019, 08:43 AM
KRE
Senior Member
 
Join Date: Nov 2011
Location: NE. Alabama
Posts: 318
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 41 Post(s)
Back up genset size depends upon needs & wants. Many believe just having the very basics is not worth the cost of a larger investment an that's fine. Then you have people who are out restoring power for every one else that will not allow their family's lives to be interrupted. The other need is for people who can not/able to haul a genset out an hook it up by their self's. Many have health issues or have family members that are bed/wheel chair ridden, who can not survive w/o electrical power. Home owners that work from home normally require more power an don't have time to drag something out during a high end conference call ect. There are many places in this country were power is not 100% 99.95% of the time. The reason many are now targeting the 15-25KW market but any unit that size or manufacturer that is sold in a box store has way higher life cycle costs compared to those sold thru other outlets. That old, We sell it but don't service it, is a clue from the gate.

Once you know how a device, system, ect operates, finding the root cause in the event chain is easy. Until then, you will always be chasing/repairing the effects. Learning is a life time event, if you want to outsmart, whatever item you want to repair.
KRE is offline  
Sponsored Links
Advertisement
 
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Power Equipment Forum : Power Equipment Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in













Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome