Do I need to ground a portable generator?

Newbie here... I know this has been covered before, but for some reason I keep reading conflicting opinions in various threads.

I bought myself a Honda EU2200i portable generator for basic emergency use - like powering a refrigerator. I noticed it does not come with GFCI outlets, but it does have a ground terminal. The Honda industrial version EB2200i does have GFCI (should I have bought that?).

I have read a little about floating and bonded neutrals and while I will continue to read more, my question is hopefully simple.

Under what circumstances would I need to use the grounding terminal on my EU2200i? I assume there is no harm in NOT using it since every video on YouTube shows it running without being connected to a 6' spike?

Thank you.
Robh is online now  
Sponsored Links
Advertisement
 
post #2 of 12 (permalink) Old 08-22-2019, 01:55 PM
Senior Member
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 221
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 35 Post(s)
A generator not connected to a building's main panel/grounding system is a "separately derived system" and should itself be grounded, providing a reference ground for all devices it serves.

Generator Grounding
tabora is offline  
post #3 of 12 (permalink) Old 08-22-2019, 02:12 PM Thread Starter
Junior Member
 
Join Date: Aug 2019
Posts: 18
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 8 Post(s)
I'm sorry Tabora...I appreciate the link, but it doesn't help. The second sentence in that link says this:
Quote:
Ground rods (grounding electrodes) are only required if the generator is a separately derived system.
So does that mean we're all doing it wrong?
Robh is online now  
Sponsored Links
Advertisement
 
post #4 of 12 (permalink) Old 08-22-2019, 05:30 PM
Senior Member
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 221
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 35 Post(s)
Quote:
Originally Posted by Robh View Post
I'm sorry Tabora...I appreciate the link, but it doesn't help. The second sentence in that link says this:

So does that mean we're all doing it wrong?
I believe that's exactly what I said... So generally, yes, most people using a portable generator running standalone (a "separately derived system") with a 3-prong or 4-prong device plugged into it are doing it wrong, because YOU can become the path to ground if there isn't a ground rod or connection to building ground at the generator. However, a 2-prong double insulated device does not have the "ground-through-you" issue. If the generator frame has a good contact with the ground, that's probably enough. I have a couple of generators on plastic carts, though, that really need at least a short, temporary ground "spike" to get a decent ground.

Last edited by tabora; 08-22-2019 at 08:02 PM.
tabora is offline  
post #5 of 12 (permalink) Old 08-22-2019, 08:39 PM
Senior Member
 
Join Date: Jun 2015
Posts: 192
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 22 Post(s)
Tabora's response was correct, it does need a ground. Until you connect it to your house load center which will pick up a ground, provide one. During an outage you'll be using extension cords to power needed loads, e.g. powering a refrigerator. I got along for years by simply "installing" (buried it) a wire from the entrance ground to where I placed the generator during outages, connecting when needed. If that's not convenient, drive a ground and provide a wire where you normally place the genset. Can you power emergency loads without a ground? Yes. Is it legal? No. Are you risking life and property? Yes. If there is an incident involving a loss and your insurance company gets involved, they will be very interested in what creative wiring you did-or didn't do.

GFCI's are certainly wonderful things and have a very deserved place. Personally in addition to them, I like nice solid copper ground wire routed around to do what it's supposed to do, carry any stray discharges back to ground, that is in addition to "interrupting" the circuit. Generally we drag out the gensets during storms when lightning strikes, surges, etc. are wandering around causing mischief.
exmar is online now  
post #6 of 12 (permalink) Old 08-23-2019, 10:05 AM
Senior Member
 
Join Date: Aug 2018
Location: Lowell area, MA
Posts: 223
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 38 Post(s)
I'm guilty of using a generator in a random, disconnected location (in a field at a park) with no added ground. I guess I could bring something (like a little spike) that could be banged into the ground, and attached to the generator's ground terminal.

Good discussion, thanks guys.
RedOctobyr is online now  
post #7 of 12 (permalink) Old 08-23-2019, 03:09 PM
Senior Member
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 221
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 35 Post(s)
Quote:
Originally Posted by RedOctobyr View Post
...I guess I could bring something (like a little spike) that could be banged into the ground, and attached to the generator's ground terminal...
I use a steel tent stake that has a solid hook to attach the ground wire. It makes a reasonable ground and fits in the battery box that's bolted to my generator cart. I have a 3' 4-gauge wire with a mechanical connector on each end.
Attached Images
File Type: jpg Stake.jpg (4.5 KB, 4 views)

Last edited by tabora; 08-23-2019 at 03:12 PM.
tabora is offline  
post #8 of 12 (permalink) Old 08-23-2019, 10:25 PM
Senior Member
 
Join Date: Jun 2015
Posts: 192
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 22 Post(s)
Trying to simplify things in my old age so got rid of two cycle chain saws and hedge trimmers. Small genset in garden cart behind one of the GT's, extension cord (double insulated of course) and appropriate electric tool(s). Two cycle engines that are only started a couple times a year don't care what octane, synthethic oil mix, stabil, etc. still a PITA! Always forget a ground stake though. :-)
exmar is online now  
post #9 of 12 (permalink) Old 08-28-2019, 08:06 PM
Junior Member
 
Join Date: Jun 2016
Location: Wisconsin
Posts: 8
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
So, I should be grounding my little inverter style generator when I am running my camper off it? How would I do that? I don't recall any kind of ground connection on it and it is basically encased in a plastic shell.
pepperpikker is offline  
post #10 of 12 (permalink) Old 08-28-2019, 08:09 PM Thread Starter
Junior Member
 
Join Date: Aug 2019
Posts: 18
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 8 Post(s)
I've read some more. No, you don't have to ground it, provided you're just plugging in a directly connected appliance or something.
Robh is online now  
Sponsored Links
Advertisement
 
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Power Equipment Forum : Power Equipment Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in













Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome