Briggs and Stratton 01938 shut down issue

So I was given this generator from a neighbor who was older and stated she never used it. Prior to moving the generator to my home I ran it at her home for about 10mins. I also changed the oil prior as it sat for about 10 years. Anyway I moved it to my house where it sat for another year. I recently got the natural gas connected so I fired it up. I noticed that there was some rust on the body of the generator and that some of the grounding for the sensors and solenoids were not functioning because of the poor ground connections. I ran some ground cables and solved that problem. I currently do not have the load side connected.

The generator will start right up and run and sounds good. I noticed that while the engine was running, the starter was engaging periodically. After about 3-4 mins, the engine shuts down and the LED flashed 4 times indicating "Engine start failure." I then found the wiring diagram online and could not see what tells the CPU the engine is running. I connected T1 and T2 wires to the load side of the circuit breaker inside the generator and tried running it with the circuit breaker on. When I do that the generator starts and runs for about 10-15 secs and shuts down. It then restarts and shuts down again continuing this pattern for a while.

When I check the voltage on the line side of the circuit breaker I noticed that the voltage is low (98v / 98v 198v). If I shut the breaker off it goes back to running for about 3-4 mins however cycling the solenoid numerous times. I would manually hold the starter wire on the solenoid till after it started then remove the wire so it would not burn up the starter.

Another note was that the earth ground that needs to connect to the house ground (or ground rod I am assuming) was not connected. It was attached to a lug which was mounted to the generator housing however that rusted off. I ran a new wire to the base of the engine and spliced it for now however there was no change. This occurs in Auto and Manuel mode.

Can somebody point me in the right direction?? Thank you in advance.

Tom
M5finally is offline  
Sponsored Links
Advertisement
 
post #2 of 9 (permalink) Old 08-16-2019, 06:47 PM
Senior Member
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 221
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 35 Post(s)
You'll probably need to disconnect the safeties/electronics and start/run the genset in "stupid" mode for a while until the generator recovers from not being run for so long. Monitor the output voltage and it will hopefully rise to about 122-127V on on each leg within an hour or so. Then you can reconnect the electric starter and other circuitry. Had a similar issue with an Onan that sat for 20 years; works perfectly after exercising it as above.
tabora is offline  
post #3 of 9 (permalink) Old 08-16-2019, 07:33 PM Thread Starter
Junior Member
 
Join Date: Aug 2019
Posts: 5
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
So your saying bypass the computer completely and run it for a while. Can I jump out the solenoid? Also what shuts down the motor?
M5finally is offline  
Sponsored Links
Advertisement
 
post #4 of 9 (permalink) Old 08-19-2019, 02:58 AM
Senior Member
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 221
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 35 Post(s)
Quote:
Originally Posted by M5finally View Post
So your saying bypass the computer completely and run it for a while. Can I jump out the solenoid? Also what shuts down the motor?
With the switch in Manual mode, you should be able to start the engine without the utility power present. Then pull the starter wire off the solenoid as you said you were already doing to eliminate the constant restart attempts, and wait for the output voltage to (hopefully) normalize. Moving the Auto/Off/Manual switch to Off should shut down the engine.

Link to manual in case you don't have it: https://c.searspartsdirect.com/mmh/p...M/L0402147.pdf
Link to troubleshooting guide: https://c.searspartsdirect.com/mmh/p...M/L0402150.pdf
See Page 23 for the Low Voltage Troubleshooting section and follow the procedure there if the simple "run it for an hour" doesn't solve the low voltage issue. Also see Page 24 for the Engine Fails To Start troubleshooting.

Last edited by tabora; 08-19-2019 at 03:05 AM.
tabora is offline  
post #5 of 9 (permalink) Old 08-19-2019, 07:40 PM Thread Starter
Junior Member
 
Join Date: Aug 2019
Posts: 5
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
The issue is even in manual mode it shuts down after about 3-5 minutes. I was wondering if I could bypass whatever shuts down the motor itself.
M5finally is offline  
post #6 of 9 (permalink) Old 08-20-2019, 05:40 PM Thread Starter
Junior Member
 
Join Date: Aug 2019
Posts: 5
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
Quote:
Originally Posted by tabora View Post
With the switch in Manual mode, you should be able to start the engine without the utility power present. Then pull the starter wire off the solenoid as you said you were already doing to eliminate the constant restart attempts, and wait for the output voltage to (hopefully) normalize. Moving the Auto/Off/Manual switch to Off should shut down the engine.

Link to manual in case you don't have it: https://c.searspartsdirect.com/mmh/p...M/L0402147.pdf
Link to troubleshooting guide: https://c.searspartsdirect.com/mmh/p...M/L0402150.pdf
See Page 23 for the Low Voltage Troubleshooting section and follow the procedure there if the simple "run it for an hour" doesn't solve the low voltage issue. Also see Page 24 for the Engine Fails To Start troubleshooting.
Thanks for the schematic it helped out big time. I will just disconnect the one wire that shuts down the motor and monitor the temp and oil.
M5finally is offline  
post #7 of 9 (permalink) Old 09-06-2019, 10:33 PM Thread Starter
Junior Member
 
Join Date: Aug 2019
Posts: 5
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 1 Post(s)
Just an update..

I replaced both 35uf capacitors and got the voltage up to 237 on both phases. The generator however, still shuts down and I get the "fail to start" warning. I jumped out the CPU and ran it without any safeties. The Genset runs fine and the voltage maintains. I still however get the fail to start warning. I ran the Genset for over an hour. The frequency is also at 60hz. I have not had a chance to load test it yet however this Hurricane almost forced me to.

Just wondering what else could be setting off the fail to start warning.

Thanks
M5finally is offline  
post #8 of 9 (permalink) Old 09-06-2019, 11:07 PM
Senior Member
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 221
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 35 Post(s)
Did you go through the entire "Engine Fails To Start" troubleshooting on pages 24-29?
tabora is offline  
post #9 of 9 (permalink) Old 09-07-2019, 12:36 PM
Super Moderator
 
motormonkey's Avatar
 
Join Date: Jul 2016
Posts: 151
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 14 Post(s)
Sounds like you're chasing intermittent symptoms. The ground issues would hint that weather and rust have likely compromised electrical connections causing the problems.

You don't fix "poor ground connections" by "running some ground cables." You fix the poor connections. Inspect and as needed, disassemble, remove corrosion, rust, etc., adjust or replace, apply some anti-corrosive/preservative like DeoxIt, and reassemble.

If you have "poor ground connections," you probably have lots of other poor connections elsewhere. Same procedure applies. Inspect and as needed, disassemble, remove corrosion, rust, etc., adjust or replace, apply some anti-corrosive/preservative like DeoxIt, and reassemble.

This is not guaranteed to solve your problems, but it is a vital first step in the troubleshooting process.
motormonkey is offline  
Sponsored Links
Advertisement
 
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Power Equipment Forum : Power Equipment Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome