post #1 of 12 (permalink) Old 07-24-2019, 10:44 PM Thread Starter
Senior Member
 
Join Date: Sep 2017
Posts: 116
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 29 Post(s)
Pulsar PG2000is Volts good, Amps low

I have a new (10 hrs run time) Pulsar PG2000IS.
It's rated for 2000Watts Peak, 1600Watts running - 13 Amps

Inverter Generator (Comparable to the Honda Eu2000is)




Found out today (using a Kill-A-Watt tool) that it stops generating power at 800watts or 7Amps. (I notice these values are half the rated value)

The voltage is fine at 123v

The Overload light never comes on at all. It just stops putting out any power at all until I unplug the device that's plugged into one of the outlets, and plug it back in.
it is not necessary to press any reset buttons or circuit breakers. Just unplugging the load and plugging it back in restores power.

I find this odd.
Anyone run into this problem before?
.
.
.

To clarify - I'm not a Predator, but one of my Generators IS
HarborFreight Predator 3500 Inverter

Last edited by Predator; 07-24-2019 at 10:48 PM.
Predator is online now  
Sponsored Links
Advertisement
 
post #2 of 12 (permalink) Old 07-25-2019, 06:39 PM
Senior Member
 
Join Date: Aug 2018
Location: Lowell area, MA
Posts: 200
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 30 Post(s)
That sure doesn't sound right, but I don't have any idea of what you could do about it. If you're within a return period, I'd take it back to the store, or contact the manufacturer if it's under warranty. I get the impression that inverter units (boards) themselves are typically just replaced if something goes wrong, and that trying to repair them may be difficult.

A long shot, but: if your load had a really bad/low Power Factor (0.5), you could be putting out 800W, but the actual load on the generator would be 1600VA. And they are really rated in VA, not Watts.

On the Kill-A-Watt, run your load again, and change to the VA display, see what that's showing before it cuts out. That's what the generator cares about, not Watts. For an electric heater, hair dryer, etc, Power Factor=1.0, so VA=Watts. But other loads will have a PF<1, so VA>Watts.
RedOctobyr is online now  
post #3 of 12 (permalink) Old 07-25-2019, 07:13 PM
KRE
Senior Member
 
Join Date: Nov 2011
Location: NE. Alabama
Posts: 303
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 38 Post(s)
Quote:
Originally Posted by Predator View Post
I have a new (10 hrs run time) Pulsar PG2000IS.
It's rated for 2000Watts Peak, 1600Watts running - 13 Amps

Inverter Generator (Comparable to the Honda Eu2000is)




Found out today (using a Kill-A-Watt tool) that it stops generating power at 800watts or 7Amps. (I notice these values are half the rated value)

The voltage is fine at 123v

The Overload light never comes on at all. It just stops putting out any power at all until I unplug the device that's plugged into one of the outlets, and plug it back in.
it is not necessary to press any reset buttons or circuit breakers. Just unplugging the load and plugging it back in restores power.

I find this odd.
Anyone run into this problem before?
.
.
.
If the voltage is in fact going away under load then returns right after the load is removed you have a connection that is opening up via heat, an may re-power as soon as it cools down. Common electrical issue, nothing more. It can be tracked down in many different ways depending your skill level, an metering or lack thereof, on hand.

Once you know how a device, system, ect operates, finding the root cause in the event chain is easy. Until then, you will always be chasing/repairing the effects. Learning is a life time event, if you want to outsmart, whatever item you want to repair.
KRE is offline  
Sponsored Links
Advertisement
 
post #4 of 12 (permalink) Old 07-25-2019, 08:40 PM
Senior Member
 
Join Date: Aug 2018
Location: Lowell area, MA
Posts: 200
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 30 Post(s)
Could you try to test for that by leaving the load connected, and seeing if it starts to come back as the connection cools? Or maybe also have something like an incandescent light connected? Something that might respond to a partial restoration of power (glowing dimly, vs a device that simply won't turn on until it gets 100V). You could also leave the Kill-A-Watt connected, to monitor what's going on as it happens.
RedOctobyr is online now  
post #5 of 12 (permalink) Old 07-25-2019, 10:01 PM
KRE
Senior Member
 
Join Date: Nov 2011
Location: NE. Alabama
Posts: 303
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 38 Post(s)
Quote:
Originally Posted by RedOctobyr View Post
Could you try to test for that by leaving the load connected, and seeing if it starts to come back as the connection cools? Or maybe also have something like an incandescent light connected? Something that might respond to a partial restoration of power (glowing dimly, vs a device that simply won't turn on until it gets 100V). You could also leave the Kill-A-Watt connected, to monitor what's going on as it happens.
You could but depending on bleed voltage it may be awhile. Bleed voltage is voltage that is present but much lower than rated. Once a connection gets hot it takes very little amperage (Voltage X resistance)to keep it hot an open.

Once you know how a device, system, ect operates, finding the root cause in the event chain is easy. Until then, you will always be chasing/repairing the effects. Learning is a life time event, if you want to outsmart, whatever item you want to repair.
KRE is offline  
post #6 of 12 (permalink) Old 07-27-2019, 09:28 AM Thread Starter
Senior Member
 
Join Date: Sep 2017
Posts: 116
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 29 Post(s)
Quote:
Originally Posted by RedOctobyr View Post
That sure doesn't sound right, but I don't have any idea of what you could do about it. If you're within a return period, I'd take it back to the store, or contact the manufacturer if it's under warranty. I get the impression that inverter units (boards) themselves are typically just replaced if something goes wrong, and that trying to repair them may be difficult.

A long shot, but: if your load had a really bad/low Power Factor (0.5), you could be putting out 800W, but the actual load on the generator would be 1600VA. And they are really rated in VA, not Watts.

On the Kill-A-Watt, run your load again, and change to the VA display, see what that's showing before it cuts out. That's what the generator cares about, not Watts. For an electric heater, hair dryer, etc, Power Factor=1.0, so VA=Watts. But other loads will have a PF<1, so VA>Watts.

Thanks for the suggestion.
I did the tests checking the VA as suggested with various appliances connected. Most times the Watts was essentially equal to VA.

That said, it may have been one appliance (A small, 1500Watt portable heater) that was causing the problem after all. Without that particular appliance connected the generator was able to run a 1550Watt / VA load.


With one caveat ......I'll mention below.

To clarify - I'm not a Predator, but one of my Generators IS
HarborFreight Predator 3500 Inverter

Last edited by Predator; 07-27-2019 at 09:37 AM.
Predator is online now  
post #7 of 12 (permalink) Old 07-27-2019, 09:30 AM Thread Starter
Senior Member
 
Join Date: Sep 2017
Posts: 116
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 29 Post(s)
Quote:
Originally Posted by KRE View Post
If the voltage is in fact going away under load then returns right after the load is removed you have a connection that is opening up via heat, an may re-power as soon as it cools down. Common electrical issue, nothing more. It can be tracked down in many different ways depending your skill level, an metering or lack thereof, on hand.

Thank you for the suggestions.
It turns out it may have been a particular appliance that may have had a power factor of less than one as suggested by RedOctobyr


I'll be testing that same small portable heater today with standard AC from a home wall socket to see what the VA and watts are that the portable generator could not handle.

To clarify - I'm not a Predator, but one of my Generators IS
HarborFreight Predator 3500 Inverter
Predator is online now  
post #8 of 12 (permalink) Old 07-27-2019, 09:33 AM Thread Starter
Senior Member
 
Join Date: Sep 2017
Posts: 116
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 29 Post(s)
A final question.......

Has anyone ever heard of a situation such as the following?

Suppose you have a small device plugged into the DC outlet on the generator......
Is there any known circuitry inside a portable Inverter Generator that might sense that something is connected to the 12vDC port and then limit the output to the AC outlets?

I did initially have a small 12vDC device plugged in when I was having the issue in the OP. But I have no idea if that could cause the generator to reduce it's available output to the AC outlets.

.
.
.

To clarify - I'm not a Predator, but one of my Generators IS
HarborFreight Predator 3500 Inverter

Last edited by Predator; 07-27-2019 at 09:45 AM.
Predator is online now  
post #9 of 12 (permalink) Old 07-27-2019, 09:45 AM Thread Starter
Senior Member
 
Join Date: Sep 2017
Posts: 116
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 29 Post(s)
One final Note on Pulsar Generators.

I have a number of generators ranging from 6250Watt Briggs and Stratton powered units to HarborFreight units and Honda Units.

This Pulsar Generator is one of my favorites. It is feature packed, has a USB outlet and all the bells and whistles of the units costing over twice as much.
It is quiet, start on first or second pull every time and runs smooth.
It is also VERY well built inside.

Provided the problem I was having was just because of one rogue appliance, it cranks out power exactly as advertised.
In addition, their Customer Service is responsive and very helpful. They were prepared to replace the generator for me with return shipping paid by them


I can highly recommend Pulsar Generators.

To clarify - I'm not a Predator, but one of my Generators IS
HarborFreight Predator 3500 Inverter
Predator is online now  
post #10 of 12 (permalink) Old 07-27-2019, 12:10 PM
Senior Member
 
Join Date: Aug 2018
Location: Lowell area, MA
Posts: 200
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 30 Post(s)
Quote:
Originally Posted by Predator View Post
A final question.......

Has anyone ever heard of a situation such as the following?

Suppose you have a small device plugged into the DC outlet on the generator......
Is there any known circuitry inside a portable Inverter Generator that might sense that something is connected to the 12vDC port and then limit the output to the AC outlets?

I did initially have a small 12vDC device plugged in when I was having the issue in the OP. But I have no idea if that could cause the generator to reduce it's available output to the AC outlets.

.
.
.
I've never dug into that, but I've also never needed to use the 12V output from my generators, either. Don't know whether it would limit anything based on DC usage. But even if it did, the DC wouldn't use much of your capacity. Even 10A of DC (the most my cigarette lighter outlet can supply) would still only be 120W.

From units I've had, that DC output is typically unregulated voltage, and is really intended just for charging batteries, not so much for running cigarette-lighter style loads.
RedOctobyr is online now  
Sponsored Links
Advertisement
 
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Power Equipment Forum : Power Equipment Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome