Kawasaki GA1800A over voltage

Hi all. Wonder if someone can shed some light on a problem in having.
I have recently acquired a Kawasaki GA1800A generator, it hadn’t run in 10 years, and after freeing the sticking valve it started right up! Engine runs sweet! The problem I’m having is that when I tested the 230v outlet just to check voltage before I plugged anything into it, the voltage was 400v!!! And 200v at the 110v socket. What would cause this over voltage ? I thought it might be the AVR but I believe if that fails it won’t produce anything! Any help would be great!
Luke is offline  
Sponsored Links
Advertisement
 
post #2 of 5 (permalink) Old 07-08-2019, 09:46 PM
Senior Member
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 177
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 26 Post(s)
First verify that it's turning at 3600RPM if you're at 60Hz (3000RPM for 50Hz). If the speed is correct, the problem is most likely the AVR. They can fail in multiple ways, with high/low/no voltage results.
tabora is offline  
post #3 of 5 (permalink) Old 07-09-2019, 03:07 AM Thread Starter
Junior Member
 
Join Date: Jul 2019
Posts: 2
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 0 Post(s)
Okay thanks will check that. If I reduce the speed of the generator, to much lower than 3000rpm the voltage does drop down ? Could this still mean that is a problem with the AVR, with the generator producing high voltage at proper rpm ?
Luke is offline  
Sponsored Links
Advertisement
 
post #4 of 5 (permalink) Old 07-09-2019, 05:26 AM
Senior Member
 
Join Date: Aug 2018
Location: Lowell area, MA
Posts: 191
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 25 Post(s)
Maybe you mean just as a test. But the generator needs to stay at 3600 RPM, to produce 60 Hz power.
RedOctobyr is online now  
post #5 of 5 (permalink) Old 07-10-2019, 04:10 PM
Senior Member
 
Join Date: Sep 2015
Posts: 131
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 14 Post(s)
Hi luke,

The function of an AVR, is to maintain a fixed output voltage in a generator. At the start, there is only a very weak remanent magnetic field in the rotor, left after the last generator operation, this field induces a very low AC voltage in the stator, which is sent to the AVR (functioning as a voltage controlled switch).AVR compares a fraction of the main output voltage with a reference fixed voltage, (set by a zener diode and an adjusting potentiometer in the AVR), if the ref voltage is higher than the gen output sample,the AVR permits to pass all the current generated to the rotor windings, increasing the magnetic field and so, the induced voltage in the stator windings. This is sent again to the AVR. As the RPM increases and the rotor magnitic field does the same, the output voltage is higher and higher up to reach the nominal voltage level.

Once reached this value (110VAC or 220VAC) independent of the RPMs (so the frequency, Hz),The AVR cuts the rotor feed current, causing a decrease in the voltage generated, which is detected in the AVR, creating a difference between the reference (higher) and the sample. Avr starts conducting again, but, if it fails to cut due to a shorted transistor or something similar, the excitation current increases up to reach a saturation point ,and in this point the output voltage remains topped. This condition is really dangerous for thr generator head, because the rotor windings are overloaded with the full voltage available applied to the rotor windings overheating them, and if this condition is maintained enough time, they will be burnt.This is for a brushed generator, for a brushless the excitation field will suffer and possibly the rotor winddings too.

All this control process is done in the generator head. The engine doesn't "know" what is happening in the other side. The engine control is the governor, which maintains the RPM's fixed , to permit to the gen head maintain a fixed frquency (talking about a non inverter generator) , independent of the impossed load from the gen head.The only communication between engine and generator head is the common shaft which transmits the resistance torque from the generator to the engine.

In few words your AVR is failing.

Regards.
Osviur is online now  
Sponsored Links
Advertisement
 
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Power Equipment Forum : Power Equipment Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome