post #1 of 25 (permalink) Old 02-18-2019, 09:31 PM Thread Starter
Junior Member
 
Join Date: Feb 2019
Posts: 11
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 4 Post(s)
hook up 20 year old generator using interlock kit

I have a 20 year old generator, 5000w, with about 20 hours on it. see the pic I want to use it through a generator interlock device (SD-H200A Square D Generator Interlock Kit).

The circuit breaker panel has the dryer circuit breakers in exactly the correct location for that interlock kit. The dryer socket is unused since we have a gas dryer, and the socket is located in what is now part of the kitchen. In other words, I have an unused dryer socket wired to the 30 amp circuit breakers on the main circuit board that line up properly for the generator interlock kit.

I want to run the generator output to that dryer socket.
--- When the utility power is on, that dryer socket would be cold, since the generator interlock device would not allow those circuit breakers to be closed (hot).
--- When the utility power goes out, the interlock device would be moved to shut off the utility power main circuit breakers, and close what used to be the dryer circuit breakers, thereby connecting the dryer socket to the main circuit breaker panel.

I need to know a good way to run the generator output to that dryer socket. The old generator does NOT have a twist connector, it just has sockets that look pretty much like a standard 120V socket except for one of the blade slots being a T. Three holes for three conductors, like the dryer socket. See the pic

= Should I make a fancy extension cord?
= Should I remove the old style generator output sockets and replace them with a more up-to-date twist connector, then build or buy that fancy extension cord?
= Should I just bite the bullet and sell the generator for cheap and buy a new generator with a twist socket? (I am considering this option because this generator is LOUD. The new inverter generators are really quiet and have electric starters) I'd still have to run a cable of some sort from the twist socket on the inverter generator to the dryer socket.
= Do the twist sockets have four conductors or three? The dryer socket has three.
Attached Images
File Type: jpg Generator 05.jpg (70.8 KB, 11 views)
File Type: jpg Generator 04.jpg (142.6 KB, 10 views)
File Type: jpg overallgen1.jpg (77.1 KB, 12 views)
Gyrobog is offline  
Sponsored Links
Advertisement
 
post #2 of 25 (permalink) Old 02-19-2019, 01:02 PM Thread Starter
Junior Member
 
Join Date: Feb 2019
Posts: 11
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 4 Post(s)
Upon further research, it appears there would be problems hooking up a generator to a 3-prong dryer socket, even if the dryer socket was being switched on and off by a generator interlock,... and,.. even though the generator only has three prong outlets. See the pics in the first post for the type of 3-prong plug on the generator.

My original idea was to forget about those 30 amp dryer circuit breakers being dryer circuit breakers, and just use them as if they had been installed specifically for use with an interlock kit. I have the interlock kit, and it will work correctly by allowing only the house feed OR the dryer circuit breakers to be on simultaneously.

I may have to forget about using the 3-prong dryer socket and just install an external L14-30R socket going to the existing dryer circuit breakers. That's a bummer because the existing set up with the dryer socket would have been so convenient. The dryer socket is about 10 feet from where the generator will be. Running the wiring from the external L14-30R socket to the circuit breaker panel is about 30 feet and will be more of a challenge to route the wiring.

The generator only has three-prong outlets. That's why I thought it would be handy to just run a 3-wire cable with a dryer plug on one end and a small three-prong 240V plug to match the generator on the other. See the pics in the first post for the type of 3-prong plug on the generator.

Any clarification on this issue would be greatly appreciated.
Gyrobog is offline  
post #3 of 25 (permalink) Old 02-19-2019, 01:58 PM
Super Moderator
 
motormonkey's Avatar
 
Join Date: Jul 2016
Posts: 152
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 14 Post(s)
You are correct that a 3-conductor 240-volt-only type circuit is not suitable for a proper 120/240 generator hookup. (no current carrying neutral) You need four conductors (ground, line, line, and neutral) to properly bring power from a generator to your house circuit.


You'll have to modify the generator to install the proper receptacle (L14-30R) and isolate neutral and ground. You'll also have to install a suitable 4-conductor generator receptacle (L14-30FI) outside your house and run a suitable four-conductor cable from that to your breaker box. Since the dryer circuit isn't in use, just disconnect the dryer wires from the dryer breaker and connect the genny circuit to it (and definitely install the interlock kit!). Ready made four-wire extension cables for use between the genny and the house are available at any decent home center.

A lot of this was covered in this thread:
https://www.powerequipmentforum.com/...ck-outlet.html

Last edited by motormonkey; 02-19-2019 at 02:00 PM.
motormonkey is offline  
Sponsored Links
Advertisement
 
post #4 of 25 (permalink) Old 02-19-2019, 07:20 PM
Senior Member
 
tabora's Avatar
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 253
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 44 Post(s)
Opinions vary ( see other thread referenced above ), but since it's only a 20amp 240V output, I would not hesitate to connect it to the properly interlocked dryer circuit breaker and the bonded panel neutral/ground bus bar, WITHOUT a separate ground rod. This assumes that the generator outlets are not GFCI, which I do not believe is the case on your generator. To quote another forum's moderator:
In a normal circuit yes it would be a problem to have a bonded neutral and ground [on the generator], but in a temporary generator feed it is much less of a concern. It is more of a theoretical issue, but given that your generator cord is going to have an insulated ground conductor, even that is somewhat implausible. You will have created a parallel neutral feed, but since we're talking a main panel, neutral and ground really are the same thing at that point. The generator being bonded is sort of like the service entrance mast or meter socket box in that the neutral and ground are bonded at multiple points through them. The neutral is technically an insulated conductor running through the mast, but it's sometimes bonded at the top of the mast where the ACSR drop lashes, bonded in the meter can to the metal box, sometimes bonded via a bonding bushing, and bonded again in the main panel; the steel framework is electrically indistinguishable from the neutral conductor itself. Adding the generator frame to what bonding already exists in the service entrance really is not a big leap.
tabora is online now  
post #5 of 25 (permalink) Old 02-19-2019, 09:44 PM
Senior Member
 
tabora's Avatar
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 253
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 44 Post(s)
Quote:
Originally Posted by Gyrobog View Post
The new inverter generators are really quiet and have electric starters.
Yes, but a quality 240V electric start inverter generator IS NOT cheap... There are actually very few, of which the Honda EU7000is @ $4500 is the most common: https://www.northerntool.com/shop/to...0183_200640183

Last edited by tabora; 02-19-2019 at 09:49 PM.
tabora is online now  
post #6 of 25 (permalink) Old 02-20-2019, 09:02 AM
Senior Member
 
Join Date: Aug 2018
Location: Lowell area, MA
Posts: 227
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 42 Post(s)
IF you can get by with 110V power, then yes, there are nice inexpensive inverter options. But for now, like tabora said, 220V inverter choices are limited, and expensive.

If HF makes a good 220V inverter unit at some point, that would get my attention. For now, my pair of little EU2000i do a great job. Quiet, clean power, and great on gas.

Last edited by RedOctobyr; 02-20-2019 at 09:12 AM.
RedOctobyr is offline  
post #7 of 25 (permalink) Old 02-20-2019, 01:58 PM Thread Starter
Junior Member
 
Join Date: Feb 2019
Posts: 11
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 4 Post(s)
Quote:
Originally Posted by tabora View Post
Yes, but a quality 240V electric start inverter generator IS NOT cheap... There are actually very few, of which the Honda EU7000is @ $4500 is the most common: https://www.northerntool.com/shop/to...0183_200640183

How about this one?

https://www.homedepot.com/p/Briggs-S...0675/301871650
Attached Images
File Type: jpg B&S Q6500.JPG (31.7 KB, 2 views)
Gyrobog is offline  
post #8 of 25 (permalink) Old 02-20-2019, 02:01 PM Thread Starter
Junior Member
 
Join Date: Feb 2019
Posts: 11
Mentioned: 1 Post(s)
Tagged: 0 Thread(s)
Quoted: 4 Post(s)
recoil start, though
Gyrobog is offline  
post #9 of 25 (permalink) Old 02-20-2019, 03:01 PM
Senior Member
 
Join Date: Aug 2018
Location: Lowell area, MA
Posts: 227
Mentioned: 3 Post(s)
Tagged: 0 Thread(s)
Quoted: 42 Post(s)
Impressive price for the specs! 5000W continuous, 6500W starting, 240V output, inverter, and $1,200.

Assuming it holds up and is reliable, that sounds pretty good.
RedOctobyr is offline  
post #10 of 25 (permalink) Old 02-20-2019, 03:50 PM
Senior Member
 
tabora's Avatar
 
Join Date: Sep 2018
Location: Cape Elizabeth, Maine
Posts: 253
Mentioned: 0 Post(s)
Tagged: 0 Thread(s)
Quoted: 44 Post(s)
Quote:
Originally Posted by Gyrobog View Post
Non-electric start, as you mentioned, and only 20A at 240V, so all you're gaining is quieter operation and some fuel economy over your Powermate.

And for what it's worth, the neutral and ground are also bonded on this one... And it appears that Consumer Reports may have it on their naughty list.
Attached Images
File Type: jpg Q6500.jpg (139.0 KB, 7 views)

Last edited by tabora; 02-20-2019 at 04:57 PM.
tabora is online now  
Sponsored Links
Advertisement
 
Reply

Quick Reply
Message:
Options

Register Now



In order to be able to post messages on the Power Equipment Forum : Power Equipment Forums forums, you must first register.
Please enter your desired user name, your email address and other required details in the form below.

User Name:
Password
Please enter a password for your user account. Note that passwords are case-sensitive.

Password:


Confirm Password:
Email Address
Please enter a valid email address for yourself.

Email Address:
OR

Log-in










Thread Tools
Show Printable Version Show Printable Version
Email this Page Email this Page



Posting Rules  
You may post new threads
You may post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On

 
For the best viewing experience please update your browser to Google Chrome